Shell Guideline on Fired Heater Tube Skin Thermocouples

Status
Not open for further replies.

Patassa

Mechanical
Oct 14, 2013
51
I'm hoping someone knows the correct interpretation of this line in the context of where to place tube skin TI's.

"In mixed flow vertical tubes, a down-flow tube is selected"

I'm unclear as to what "mixed flow" means in this context. This is a naphtha tower reboiler.

Thank you
 
Replies continue below

Recommended for you

That refers where the flow in some tubes is up and in others it is down. Select a tube where the flow is down.
 
Terms used in references to these tubes are downcomers and risers.
 