Dear All,
I have a 10" r/c shear wall where the starter bars are cast in the wrong location by 4" over the entire length of the wall. The wall is in a basement and the architect will allow us to increase the wall thickness to 14" in the basement only. ACI 12.14.2.3 allows non contact lap splices up to the smaller of 6" or 1/5 the length of the lap splice for flexural members.
I was thinking of cranking the outside bar at a 1:6 slope and leaving the inside bar as is while using a non-contact lap splice. In the location of the crank, I'm thinking a capping beam would also be useful to confine the crank. Is this an appropriate detail?
Thanks
I have a 10" r/c shear wall where the starter bars are cast in the wrong location by 4" over the entire length of the wall. The wall is in a basement and the architect will allow us to increase the wall thickness to 14" in the basement only. ACI 12.14.2.3 allows non contact lap splices up to the smaller of 6" or 1/5 the length of the lap splice for flexural members.