Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

shear wall reinfocement 1

Status
Not open for further replies.

swelm

Structural
Joined
Oct 16, 2006
Messages
70
hi everybody

i used ubc 79 and ACI 318-99
I HAVE DHEAR WALL IN MULTISTORY BUILDING UNSAFE FOR THE SHEAR RATIo the arch enginneer refuse to incease the width of wall

i hear we can add stuirrps in the shear wall to be safe in shear

but i do not know what is the equation to calculate that and what is the condition ?

can you help me?
 
Is that really UBC 79? Or did you mean UBC 97?

Either way, ACI 318-99 should not be used as it is not referenced by the earlier UBC 97.

But in ACI - see section 11.10 for shear reinforcing of walls. Specifically see 11.10.2 which refers you to Equations (11-1) and (11-2), sections 11.10.5, 11.10.6 and 11.10.9.

Hope this helps.

 
PCA published a booklet which thoroughly explained the ACI provisions for shear walls. The booklet is called "Design Provisions for Shear Walls." It is available from PCA's web site. Search for RD028. This should bring you to a page of "Free Publications."
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top