Shear strength acc. ACI 318R-02

Status
Not open for further replies.

bender36

Structural
Joined
Mar 5, 2007
Messages
12
Location
DE
Hi,

the shear strength provided by concret Vc is given in clause 11.3.1.1. The version which I have says:

Vc=2*(sqrt(fc')/6*bw*d

in the internet I found:

Vc=sqrt(fc')/6*bw*d, but realted to the same code release.

Same appwears for the limit of Vs (clause 11.5.6.9):

Vs=8*sqrt(fc')*bw*d

and

Vs=2/3*sqrt(fc')*bw*d

WHAT IS CORRECT ?

Thank you very much,

Martin
 
Upgrade to the latest edition and go metric. ACI 318M-05.
 
I'm not sure where you get the /6 in the Vc formula.

ACI 11.3.1.1, Equation 11-3 shows:

Vc = 2([√]f'c)bwd

The value in section 11.5.6.9:

Vs = 8([√]f'c)bwd
is a maximum limit on your steel shear reinforcing contribution.

I don't see where there is a Vs = 2/3([√]f'c)bwd

Vc and Vs are two different things.

 
bender35,

When you use a new formula that you are no sure about, check it to make sure it makes sense. In your case a higher area would have resulted in a lower shear capacity - obviously something was wrong.

It doesnt work so well on this formula, but usually putting the units into the formula should give you the correct units as a result (i.e kips/lbs for a force or psi for a stress).
 
Check in ACI 318-05 (SI units), you will find:
11.3.1.1, Equation 11-3
Vc = 0.17(?f'c)bwd
11.5.7.9:
Vs = 0.66(?f'c)bwd
 
the first you mention for Vc and Vs are in imperial units, the second are in Metric units
 