ishvaaag
Structural
- Aug 17, 2001
- 3,665
You determine phiVc per 11.11.2.1 of 11.11.2.2 and find your Vu is less than that. Let's call this phiVc1. Then, if you meet the geometrical conditions therein stated, as per 11.11.3 you are "permitted" to reinforce in shear by a method that only acknowledges a lower design shear stress, i.e., a lower phiVc, let's call it phiVc2, that may not meet your Vu above; in fact a design shear stress that when designing reinforcement for punching shear determines where such reinforcement becomes already unnecesary.
It is your interpretation of the code that whenever the lower phiVc2 does not meet your Vu -but is still met by phiVc1- the code makes mandatory to reinforce for punching shear by the stated method? Note that if so it might be making void the use of phiVc1 to determine a thickness without shear reinforcement, for anywhere the plate is not meeting through the corresponding phiVc2 the standing Vu you would be being asked to reinforce in shear, i.e., asked reinforcement, and it would be the scheme for shear reinforcement with the limit reaction what would be determining how to proceed.
Also, by other codes one-way shear checks were (or are still) ASKED AS WELL when the slab is in two way action. Think for example in a slender footing in ACI 318 08. Is it your understanding that by the present ACI 318 08 such checks for one-way shear have been entirely forfeited when in a two-way behaviour of the slab or footing?
It is your interpretation of the code that whenever the lower phiVc2 does not meet your Vu -but is still met by phiVc1- the code makes mandatory to reinforce for punching shear by the stated method? Note that if so it might be making void the use of phiVc1 to determine a thickness without shear reinforcement, for anywhere the plate is not meeting through the corresponding phiVc2 the standing Vu you would be being asked to reinforce in shear, i.e., asked reinforcement, and it would be the scheme for shear reinforcement with the limit reaction what would be determining how to proceed.
Also, by other codes one-way shear checks were (or are still) ASKED AS WELL when the slab is in two way action. Think for example in a slender footing in ACI 318 08. Is it your understanding that by the present ACI 318 08 such checks for one-way shear have been entirely forfeited when in a two-way behaviour of the slab or footing?