hangingchad
Structural
- Dec 15, 2000
- 1
I have a concrete box type structure that is approximately 16' inside from wall to wall and 40' tall and subjected to earth and water pressure on the outside. The ACI code special provisions for walls for design of shear perpendicular to the face of the wall references the engineer to the section of the code for "Special Provisions for Slabs and Footings." For the condition where the wall is governed by beam action and each critical section to be investigated extends in a plane across the entire width, one is referred back to the code provisions for beams. These provisions require a minimum area of shear reinforcing with exceptions, one of which is slabs and footings. Does this mean that minimum shear reinforcing is not required in a wall even though each critical section is designed as a beam? Even if the wall is spanning primarily one way? The commentary says the reason that minimum reinforcing is not needed in slabs is because of the ability of redistribution of stress, etc but I don’t see that possibility in a one way slab.