I just went throgh IEEE C37.96-1988 4.2.17. it says that 10% slope for percentage-differential relay setting, and the pick-up setting of the relay should be 10%-20% of motor FLA (for ordinary overcurrent relays in a diiferential circuit to provide differential protection to large motors). For flux-balancing differential schemes, relays should be set in accordance with instructions for seeting device 50G.
My understanding is, the latter scheme uses non-percentage differentila relay. Is that right?