I already posted this topic but in the wrong section of this forum so I'll do here again. This is first time I deal with this type of relay (I've met ABB, Areva, Siemens) and we have problem during the motor start-up. Since that start time is longer than definite time set for 50/51 the protection trips due to 50/51 during start-up. The real motor start current is greater than threshold of 50/51.
My question is there any possibility to disable 50/51 (or to double like for ABB REM610) during start-up? Motor data are 6,6kV, 500kW, 53A.
Thanks
I already posted this topic but in the wrong section of this forum so I'll do here again. This is first time I deal with this type of relay (I've met ABB, Areva, Siemens) and we have problem during the motor start-up. Since that start time is longer than definite time set for 50/51 the protection trips due to 50/51 during start-up. The real motor start current is greater than threshold of 50/51.