I should set in a industrial plant the 50N elements protecting many motors ranging from 300 kW to 4000 MW.
The system voltage is 11 kV and the ground current is limited to 600 A. The customer decided to use 50/1 cl 1 measurement (!)toroidal CT to feed the relay ground elemnts.
How sensitive can be set the 50N threshold?
What I would propose is 10% of the tore CT ratio (so 5 A) with a 100 ms delay to avoid spurious trips due to the cable capacitive currents. I wonder if a smaller threshold could be used. What's the limiting factor?
With a 5 Amps threshold I think we should already protect 99% of the motor winding.