Robert789
Electrical
- Feb 20, 2002
- 34
I'm evaluating a customer's request to install a 400 HP motor for de-barking trees at a sawmill on our distribution system. I've calculated the voltage dip due to locked rotor amps of the motor and determined that it would not be appropriate to allow it to start at full voltage (about 5.6% dip on 12.47 kV primary). It may be appropriate to allow the motor if it employs a soft start to reduce starting current.
I am concerned about what will happen should the sawmill become bogged down, or stall, due to excessive load (too much material placed in it at once). My assumption is that the soft starter would not provide any benefit in this case, and the motor current would approach the locked rotor amps value. Is this correct, or does some other factor prevent this from being a problem?
I am concerned about what will happen should the sawmill become bogged down, or stall, due to excessive load (too much material placed in it at once). My assumption is that the soft starter would not provide any benefit in this case, and the motor current would approach the locked rotor amps value. Is this correct, or does some other factor prevent this from being a problem?