Safety valve selection hot water

Status
Not open for further replies.

nicolai

Mechanical
Joined
Sep 27, 2000
Messages
42
Location
NA
Good day folks
who can direct me to applicable source or guideline...

I need to select pressure safety relief valve for high temperature hot water system (not steam) operating 188 °F (87°C )

The vessel volume is 1,300 gallon ( 5,000 liter )
The hot water source is a boiler high temperature liquid circulating a through plate heat exchanger with capacity of 100,000 btu/hr (300 kW)
On what base is the selection of adequate safte valve carried?
is their selection charts / nomographs available for this purposes?
many thks
 
Firstly, What is the applicable Construction Code?

Examples;-
ASME I - Power (fossil fired) Boiler
ASME VIII - Unfired (process) Vessel

I suspect, from your brief description, you may have a heating boiler acc. to ASME IV - Appendix 4A of this specification provides details of how to determine the size of pressure relief valve required from capacity criteria in BTU/h etc.

It is very impotant you establish what design code applies.

Note also there is a separate forum for safety relief valves, buts its OK to continue here.



*** Per ISO-4126, the generic term
'Safety Valve' is used regardless of application or design ***

*** 'Pressure-relief Valve' is the equivalent ASME/API term ***
 