Diborane
Chemical
- May 3, 2005
- 16
I recently completed sizing the SRV flow requirements for an ASME stamped vessel. One of the cases that I checked was for external fire causing the vaporization of the contents according to API 521 3.15.
My work was then sent for review to a senior engineer. He stated that I did not need to size an SRV on the reactor for the fire case.
The SRV size needed for the fire case is larger than any of the other cases looked at.
Isn't sizing for an external fire required for all ASME stamped pressure vessels? If not what cases allow you to not to have this protection? Does it matter if there aren't any likely scenarios where flammable materials would be near the vessel?
My work was then sent for review to a senior engineer. He stated that I did not need to size an SRV on the reactor for the fire case.
The SRV size needed for the fire case is larger than any of the other cases looked at.
Isn't sizing for an external fire required for all ASME stamped pressure vessels? If not what cases allow you to not to have this protection? Does it matter if there aren't any likely scenarios where flammable materials would be near the vessel?