avogel
Electrical
- May 9, 2008
- 18
I am in the US, so hoping to get some thoughts from an NEC compliance perspective. We need to run a telephone cable and the only route is a 20kV cable tray with Type MC cable.
392.6 allows you to run Class 2 circuits in the same cable tray if the cables >600V are Type MC, however it appears article 300 is superseded by wiring methods for power-limited cables, Article 725
725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors,
and Medium-Power Network-Powered Broadband
Communications Cables.
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compartment,
enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light,
power, Class 1, non–power-limited fire alarm circuits, and
medium-power network-powered broadband communications
circuits unless permitted by 725.136(B) through (I).
(B) Separated by Barriers. Class 2 and Class 3 circuits
shall be permitted to be installed together with the conductors
of electric light, power, Class 1, non–power-limited fire alarm
and medium power network-powered broadband communications
circuits where they are separated by a barrier.
So, (B) permits Class 2 to be installed with power if the circuits are separated by a barrier. But the Code has already established, MC is not defined as a "barrier."
(G) Cable Trays. Class 2 and Class 3 circuit conductors
shall be permitted to be installed in cable trays, where the
conductors of the electric light, Class 1, and non–powerlimited
fire alarm circuits are separated by a solid fixed
barrier of a material compatible with the cable tray or
where the Class 2 or Class 3 circuits are installed in Type
MC cable.
So, (G) specifically permits installing Class 2 circuits in MC cable to separate only from electric light, Class 1, and non-power-limited fire alarm circuits. Intentially leaving out "power" circuits that it listed in (B). Why is this distinction made? No where else in the NEC is "electric light" even defined or mentioned. In my mind, the rationale behind protecting the cable physically with a flimsy tin barrier would justify permitting using armored cable in the same tray with a power circuit that is also type MC.
I'm starting to wonder what use artciles 725-800 are even for, people who have no business governing electrical installations.
Any thoughts?
392.6 allows you to run Class 2 circuits in the same cable tray if the cables >600V are Type MC, however it appears article 300 is superseded by wiring methods for power-limited cables, Article 725
725.136 Separation from Electric Light, Power, Class 1,
Non–Power-Limited Fire Alarm Circuit Conductors,
and Medium-Power Network-Powered Broadband
Communications Cables.
(A) General. Cables and conductors of Class 2 and Class 3
circuits shall not be placed in any cable, cable tray, compartment,
enclosure, manhole, outlet box, device box, raceway,
or similar fitting with conductors of electric light,
power, Class 1, non–power-limited fire alarm circuits, and
medium-power network-powered broadband communications
circuits unless permitted by 725.136(B) through (I).
(B) Separated by Barriers. Class 2 and Class 3 circuits
shall be permitted to be installed together with the conductors
of electric light, power, Class 1, non–power-limited fire alarm
and medium power network-powered broadband communications
circuits where they are separated by a barrier.
So, (B) permits Class 2 to be installed with power if the circuits are separated by a barrier. But the Code has already established, MC is not defined as a "barrier."
(G) Cable Trays. Class 2 and Class 3 circuit conductors
shall be permitted to be installed in cable trays, where the
conductors of the electric light, Class 1, and non–powerlimited
fire alarm circuits are separated by a solid fixed
barrier of a material compatible with the cable tray or
where the Class 2 or Class 3 circuits are installed in Type
MC cable.
So, (G) specifically permits installing Class 2 circuits in MC cable to separate only from electric light, Class 1, and non-power-limited fire alarm circuits. Intentially leaving out "power" circuits that it listed in (B). Why is this distinction made? No where else in the NEC is "electric light" even defined or mentioned. In my mind, the rationale behind protecting the cable physically with a flimsy tin barrier would justify permitting using armored cable in the same tray with a power circuit that is also type MC.
I'm starting to wonder what use artciles 725-800 are even for, people who have no business governing electrical installations.
Any thoughts?