Gentlemen,
I am designing a building wherein the service is delivered at 34.5kV metered at the utility company yard on-site. I am routing this on-site through a series of Manholes to a point adjacent the building. I am bringing in two, 3 phase circuits to feed through a primary feed selector transfer switchgear lineup. This will subsequently feed through SF6 filled sectionalizing switches to subfeed the series of substations I need to transform to my utilization Voltage of 480Y/277V,3ph,4w.
This is my question:
The Apron level finished surface elevation exterior to the building is at +26.5'. My finished floor elevation where the switchgear will be located is at +4.5'. The switchgear is 22 feet, (about 7 meters), below the top of the manhole. Even if I use a fairly deep manhole of say 8 to 10 feet and have the conduit exit some distance above the manhole bottom, I am still concerned about water entering the conduit and syphoning down to the lower level. What is the best conduit/cable sealing system that you have experience with?
There are numerous foam sealants that are used to fill such openings, however..., and this is the kicker. These manholes are located at an airport gate apron. they are within the fueling port distance requirement that makes any area below grade, a Class 1, Division 1 atmosphere. Do any of you gents have any experience with a device or assembly that will seal a conduit and cable entry from a manhole? I've Googled till I'm light headed, and the manufacturers I am familiar with, Appleton, O-Z Gedney, don't have this configuration or size.
The cable will be 35kV MV-90, 133%,XLP with PVC jacket, #4/0 AWG max. (3)-1/c cables in a 4" PVC schedule 40 conduit with the conduit banks concrete encased.
Any guidance is appreciated,
EEJaime
I am designing a building wherein the service is delivered at 34.5kV metered at the utility company yard on-site. I am routing this on-site through a series of Manholes to a point adjacent the building. I am bringing in two, 3 phase circuits to feed through a primary feed selector transfer switchgear lineup. This will subsequently feed through SF6 filled sectionalizing switches to subfeed the series of substations I need to transform to my utilization Voltage of 480Y/277V,3ph,4w.
This is my question:
The Apron level finished surface elevation exterior to the building is at +26.5'. My finished floor elevation where the switchgear will be located is at +4.5'. The switchgear is 22 feet, (about 7 meters), below the top of the manhole. Even if I use a fairly deep manhole of say 8 to 10 feet and have the conduit exit some distance above the manhole bottom, I am still concerned about water entering the conduit and syphoning down to the lower level. What is the best conduit/cable sealing system that you have experience with?
There are numerous foam sealants that are used to fill such openings, however..., and this is the kicker. These manholes are located at an airport gate apron. they are within the fueling port distance requirement that makes any area below grade, a Class 1, Division 1 atmosphere. Do any of you gents have any experience with a device or assembly that will seal a conduit and cable entry from a manhole? I've Googled till I'm light headed, and the manufacturers I am familiar with, Appleton, O-Z Gedney, don't have this configuration or size.
The cable will be 35kV MV-90, 133%,XLP with PVC jacket, #4/0 AWG max. (3)-1/c cables in a 4" PVC schedule 40 conduit with the conduit banks concrete encased.
Any guidance is appreciated,
EEJaime