Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Roof pneumatic test on Alumunium Dome Roof Tank

Status
Not open for further replies.

Syahar1975

Mechanical
Joined
Feb 3, 2011
Messages
224
Location
ID
Dear Experts,

I am reviewing a tank construction drawings for the next months project.

I found in the approved the drawing 2 units 50 M dia. x 20 M Ht Demin. Water storage tank with Alumunium Dome Roof with 3 - 12" PVSV on it.

The design pressure is 20 mBar and there is pneumatic test at 1.25 x design pressure.

I did many times pneumatic test for steel roof but never on ADR. I am very much doubt we can achieve 25 mBar test pressure without leaks.

Your comments is appreciated.

Syah

 
I would ask the dome roof suppliers that are active in your area.
 
Given that 25 mBar is about 52 pounds per square foot and the dome weight is about 3 pounds per square foot, I see this a a real challenge for a standard aluminum dome. Best get with the tank designers ( why the pressure for a demin water tank ? ) vendors ( is it possible to hole 25 mBar? ).
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top