Have a project where we are installing a new roof on a building (currently doesn't have one). It is an old load bearing brick masonry building. Planning to use C-purlins at the existing joist pockets with some modified connectors....problem I am running into is this. The contractor who was hired before me (I know - wrong order), quoted the job with 8" C's (14 gage) at 3 feet. I have performed calcs for this and checked vs light gage framing tables and it just doesn't work....not even close. Calcs match what I see in tables and RISA, but the contractor brings up a good point. You see this size purlin in metal buildings all the time spaced at around 5 feet. Normally Z purlins, but the section modulus is very close. I know that there is some flexural reduction due to continuity of the roof joists over main frames, but it really doesn't reduce moment that much. Am I missing something really obvious? Maybe I've miscalculated or something...