i do not have the resources or time or (brain power maybe) to analyze the entire steel building done by third party 20 years ago. So.....
the utmost top roof members (8" deep z channels) failed under a heavy snow load (which the building was not designed for...apparently didnt have to be because of county lines, etc..etc..). Designing the fix, we are replacing the failed z channels with much bigger members (huge conservative 50# snow load), basically adding around 9000 lbs of dead load to the structure. Needless to say, the big girts holding up these new beams need to posted midspan under this load...
Im in SDC D... i would like to use the post as a cantilever (omf?) to resist the additional seismic loading from the additional weight of the new beams ONLY ... seems ASCE7 allows OMF 12.2.5.7... could flag pole design be used?? horrible R value yes... I cant make head nor tails of the code... any input is appreciated... and yes, i realize that by tributary rule, the posts should take half of ALL the building lateral, but for sake of this design... lets go with it!? (still attempting to read the old microfiched steel building plans to decipher the loadings... maybe wind still controls! doubt it....cant read it anyways...)
the utmost top roof members (8" deep z channels) failed under a heavy snow load (which the building was not designed for...apparently didnt have to be because of county lines, etc..etc..). Designing the fix, we are replacing the failed z channels with much bigger members (huge conservative 50# snow load), basically adding around 9000 lbs of dead load to the structure. Needless to say, the big girts holding up these new beams need to posted midspan under this load...
Im in SDC D... i would like to use the post as a cantilever (omf?) to resist the additional seismic loading from the additional weight of the new beams ONLY ... seems ASCE7 allows OMF 12.2.5.7... could flag pole design be used?? horrible R value yes... I cant make head nor tails of the code... any input is appreciated... and yes, i realize that by tributary rule, the posts should take half of ALL the building lateral, but for sake of this design... lets go with it!? (still attempting to read the old microfiched steel building plans to decipher the loadings... maybe wind still controls! doubt it....cant read it anyways...)