Hi all,
Would like to enquire on whether it is possible to calculate resulting room rh from room load and coil capacity?
There is a lot of shortage in terms of latent capacity but a lot of excess when it comes to sensible. There are concern on humidity on this room exceeding allowable tolerance.
Would like to enquire on whether it is possible to calculate resulting room rh from room load and coil capacity?
Room heat load @ 24C 17CWB | ||
btu | kw | |
Total Capacity | 5,217 | 1.529 |
Sensible Capacity | 2,228 | 0.653 |
Latent Capacity | 2,989 | 0.876 |
Room condition | 24C 17CWB | |
SHR: 0.42 |
Coil Capacity | btu | kw |
Total Capacity | 8,325 | 2.440 |
Sensible Capacity | 7,574 | 2.220 |
Latent Capacity | 750 | 0.219812 |
On coil condition | 25CDB | |
18CWB |
There is a lot of shortage in terms of latent capacity but a lot of excess when it comes to sensible. There are concern on humidity on this room exceeding allowable tolerance.