Hey all,

I've been looking through some manufacturers catalogues (namely Bailey) and they only provide the lateral load capacity where the load is applied by a single stud. Does anyone know the approach to determining the capacity for when the load is applied by a steel stud post with multiple ply's? I'm trying to determine whether or not the use of a clip from the steel stud directly into the steel beam above is necessary, or if the two screws will suffice.

Thanks
 
Replies continue below

Recommended for you

I believe their capacities are also based on stud spacing as well correct? I believe that you can use those capacities to back calculate a moment resistance of the track per foot of length. I'm fairly certain is is track leg bending that is the governing factor in their published loads.
 
My suspicion is that most point loads from windows or door jambs would require a separate deflection clip.
 
XR250 said:
My suspicion is that most point loads from windows or door jambs would require a separate deflection clip.

That's always my assumption. If the point load from the jamb is less than those single stud capacities, great. But it usually isn't. So I just specify an independent deflection clip with the required capacity (don't try to combine them - the stiffness is likely to be too different to make it meaningful).
 
CFSEI has a good technote on the design of the deflection tracks: Link

As others already noted for jamb stud assemblies you usually end up needing to do a discrete deflection clip.

I'm making a thing: (It's no Kootware and it will probably break but it's alive!)
 
Right, I usually do spec a clip but we've received shop drawings for steel studs from other engineers and they don't specify clips in situations that I believe they would be needed. I want to make sure I'm not adding an unnecessary cost to jamb studs (although the cost may be minor).
 