bdn2004
Electrical
- Jan 27, 2007
- 802
I'm reading an automatic switching procedure that will tie two 4160V motor busses together with an automatic relay on the the tie breaker. Each bus has (4) four 1000 Hp motors connected to it. Each bus is fed by it's own 10MVA, 15kV -4160V three phase transformer. It's in a main-tie-main configuration.
For example, this situation would occur if a primary feeder breaker to one of the 10MVA transformer's tripped.
It says...
The system will allow the tie breaker to close provided that the disconnected bus voltage is within 20 degrees of the powered bus voltage and the transfer occurs within a 10 cycle window.
Here's my question...where does that bus voltage on the disconnected bus come from? How long will that voltage be on the bus? Do the spinning motors that just lost their power source become a generator and supply a voltage into the bus? What is the voltage? Any info about this would be helpful.