Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Residential sprinklers

Status
Not open for further replies.

sprinkle2013

Computer
Joined
Aug 1, 2013
Messages
8
Location
US
In a 13r design with residential heads in a heated corridor outside the dwelling units, would I have to calculate 5 heads at a .10 density? Is there anything that allows the use of .05 density?
 
This is for 13R and not 13.

You may use residential sprinklers in the corridors outside the dwelling unit but the discharge must be the higher of 1)a density of .10 gpm or 2)the discharge required for the listing. Given that corridors are most often are narrow and rectangular this will most often require you to discharge at the listing and not the density.

The density of .05 gpm is only valid inside the dwelling units.

For example Vikings freedom residential pendent sprinkler vk466 (k5.2)
With sprinklers spaced 19' apart in a corridor 6' wide coverage would be 114 sq ft which would require a discharge of 11.4 gpm to obtain a density of .10.

But the listing requires a minimum discharge of 20.0 gpm @ 14.8 psi.

20.0 gpm is higher than 11.4 so you would use the minimum discharge of 20.0 gpm using four sprinklers in accordance with the listing.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top