spats
Structural
- Aug 2, 2002
- 655
I have been tasked with designing the removal of a load bearing CMU wall. The 8" wall is capped with an 8"x12" poured concrete tie beam, and there are 16"x16" pilasters in the wall at 20' on center. They would like to remove one section of wall between pilasters by retaining the tie beam, and through-bolting steel reinforcing channels each side of the tie beam. Problem is, since the pilaster flushes to one side of the wall, one of the channels is not able to bear on the pilaster. See attached detail.
I don't think I can get a strong enough seat under the unsupported channel. I figure if I through-bolt the channel to the tie beam at the pilaster with enough fasteners, then the channel's end reaction will be transferred to the pilaster through the tie beam. However, it bothers me that the thing I'm supporting (tie beam) is being used to support the reinforcing member itself. Anybody see a problem with this?
I don't think I can get a strong enough seat under the unsupported channel. I figure if I through-bolt the channel to the tie beam at the pilaster with enough fasteners, then the channel's end reaction will be transferred to the pilaster through the tie beam. However, it bothers me that the thing I'm supporting (tie beam) is being used to support the reinforcing member itself. Anybody see a problem with this?