TheRocketScientist
Mechanical
- Feb 19, 2009
- 20
Test wall outside the building was wired by others before me. From the building come 5 wires- 3 are L1 L2 L3 of 3-phase 240V AC, a 4th wire serves as a Neutral for the 240V AC which gives 125V AC off 2 legs and 210V AC off the 3rd "crazy" leg. These come from a known breaker panel in the building.
The other 2 feed wires appear to be unused and show no voltage.
I am using the 240V AC 3-phase to run a 1/2 HP test motor mounted to a wood wall some 20 ft from the building. The 125V leg runs the timer and relay.
The lack of earth ground wire worried me, so I ran a green wire from DUT [Device Under Test] housing to the feed conduit, which enters the earth for feed from the building- just in case something bad happens to the motor. At least the errant voltage would have a path to earth other than thru me.
Does this seem adequate? Kosher? Exceedingly inadequate?
the goal is to prevent death/ injury in the unlikely event that something goes horribly awry with the motor or its wiring.