I was hoping to get input on a situation my site encountered last week.
System - VCP-W Breaker with ABB TPU relay. Distributes 13.2KV directly to 5 Oil Switches and a line up of MV Switches. Each of the Oil Switches feed to 1000KVA D-Y oil filled transformer. The MV switches have a Main switch on it. The Main feeds 4 feeder MV switches. 3 of the MV switches feed 500KVA D-Y transformers and 1 feeds some rectifiers. I hope that makes sense.
We had some maintenance performed on the switches and had the above circuit de-energized.
We went to energize the VCP-W breaker with all downstream switches closed and the TPU relay tripped on a 51N (time overcurrent on the neutral phase).
51N setting: PU 50amps and 1s I2T.
Fault information in the relays history was that the relay tripped after 5seconds at 72amps.
We closed the breaker again and the same thing happened.
After several hours we found that the Phase A fuse in the Main MV switch was not put back in.
Questions.
Is this proper protection? If a fuse opened downstream by a fault or if someone forgot to put it back in after maintenance would I want the relay to trip off the breaker causing an outage on the entire circuit? Is the 51N setting to low?
Let me know if there are any questions and thanks.
I was hoping to get input on a situation my site encountered last week.
System - VCP-W Breaker with ABB TPU relay. Distributes 13.2KV directly to 5 Oil Switches and a line up of MV Switches. Each of the Oil Switches feed to 1000KVA D-Y oil filled transformer. The MV switches have a Main switch on it. The Main feeds 4 feeder MV switches. 3 of the MV switches feed 500KVA D-Y transformers and 1 feeds some rectifiers. I hope that makes sense.
We had some maintenance performed on the switches and had the above circuit de-energized.
We went to energize the VCP-W breaker with all downstream switches closed and the TPU relay tripped on a 51N (time overcurrent on the neutral phase).
51N setting: PU 50amps and 1s I2T.
Fault information in the relays history was that the relay tripped after 5seconds at 72amps.
We closed the breaker again and the same thing happened.
After several hours we found that the Phase A fuse in the Main MV switch was not put back in.
Questions.
Is this proper protection? If a fuse opened downstream by a fault or if someone forgot to put it back in after maintenance would I want the relay to trip off the breaker causing an outage on the entire circuit? Is the 51N setting to low?
Let me know if there are any questions and thanks.