INBCPE
Mechanical
- Mar 18, 2001
- 58
Hello,
I have a project where the owner wants rooftop units added to his building. Three of the spots have steel beam construction that can be reinforced with WT's (ala Miller) and additional purlins.
The fourth roof is a little more difficult, and he has no alternative position for the new unit. This roof is constructed of 18" bar joists 4 ft o.c., 27' long, with your classic gypsum built up roof. I checked my copy of the 60 year manual and the existing joist won't carry the additional load.
I don't have the access or room to get 2 new beams into position to carry the new load. I see two other alternatives. I can either reinforce the existing joists, or wrestle some new bar joists into position. New bar joists are low on my list due to space constraints in the layout of the building. I would need a crane to get them through a 3rd story window, and the pick would either involve a long run from a major street over power lines or block the local police department parking lot. Yes, reinforcing the existing joists is labor intensive, but in this case it's the less expensive alternative.
I am looking for the following advice:
1. Is there another alternative that I'm missing.
2. Is the following reinforcement plan viable:
a. Estimate current roof loads.
b. Produce shear/moment diagrams for existing joist.
c. Calculate shears and moments for the additional load.
d. Superimpose shears and moments.
e. Design reinforced supports at end reactions.
f. Determine the additional area of diagonal web members (angle or tubing shapes) required to satisfy additional shear requirements.
g. Determine additonal area of chord reinforcement (plate or shapes) required for additional moment.
h. Determine all weld lengths and cross sections required to satisfy all loads.
Any advice or story from personal experience is appreciated.
I have a project where the owner wants rooftop units added to his building. Three of the spots have steel beam construction that can be reinforced with WT's (ala Miller) and additional purlins.
The fourth roof is a little more difficult, and he has no alternative position for the new unit. This roof is constructed of 18" bar joists 4 ft o.c., 27' long, with your classic gypsum built up roof. I checked my copy of the 60 year manual and the existing joist won't carry the additional load.
I don't have the access or room to get 2 new beams into position to carry the new load. I see two other alternatives. I can either reinforce the existing joists, or wrestle some new bar joists into position. New bar joists are low on my list due to space constraints in the layout of the building. I would need a crane to get them through a 3rd story window, and the pick would either involve a long run from a major street over power lines or block the local police department parking lot. Yes, reinforcing the existing joists is labor intensive, but in this case it's the less expensive alternative.
I am looking for the following advice:
1. Is there another alternative that I'm missing.
2. Is the following reinforcement plan viable:
a. Estimate current roof loads.
b. Produce shear/moment diagrams for existing joist.
c. Calculate shears and moments for the additional load.
d. Superimpose shears and moments.
e. Design reinforced supports at end reactions.
f. Determine the additional area of diagonal web members (angle or tubing shapes) required to satisfy additional shear requirements.
g. Determine additonal area of chord reinforcement (plate or shapes) required for additional moment.
h. Determine all weld lengths and cross sections required to satisfy all loads.
Any advice or story from personal experience is appreciated.