SteelPE
Structural
- Mar 9, 2006
- 2,759
I am in the process of designing an addition to an existing building. Building Code is IBC 2015/ASCE7-10. The new addition is higher than the existing structure which is going to impose a significant snow drift onto the existing. By some miracle, we have a water stained version of the existing design documents.
Normally we would install new joists in-between the existing joists in order to support the new load imposed by the drift. This is great, however, there is a specific space where getting into the space to do this style of reinforcing is prohibited (any reinforcing in this area is not allowed). So now we are required to come up with a different method to reinforce the existing roof. We do have access to approximately 18’-0” of the 38’-4” long existing joists (just under ½ of the joists length):
Lowering the addition is not allowed.
Framing a new roof on top of the existing roof is not allowed.
Any type of reinforcing inside of the prohibited space is not allowed due to access issues.
In talking this over with my colleague, we have come up with a method that may work… although it is a little sketchy. We are proposing to introduce new beams in-between the existing roof joists. These members will only be applied above the space that we can access (which is roughly the length of the snow drift). These new members will be supported by stub columns and new support beams that will be 4” below the existing joist bottom chord (this is to allow the existing joists to deflect and not be accidentally supported by the new support beam and cause a stress reversal in the existing joist).
I think this is the best solution that we can possibly come up with. It checks off lots of boxes, however, I am slightly nervous about introducing a new support system in-between the existing joists that will be supported at mid span of the existing joists (thinking that we may still end up with some stress reversal due to increase stiffness of the support system at this location). I can easily design the new support system to support all of the loads in the bay if necessary.
Does anyone have any comments on the proposed plan? Has anyone attempted a similar method of reinforcement in the past?
Normally we would install new joists in-between the existing joists in order to support the new load imposed by the drift. This is great, however, there is a specific space where getting into the space to do this style of reinforcing is prohibited (any reinforcing in this area is not allowed). So now we are required to come up with a different method to reinforce the existing roof. We do have access to approximately 18’-0” of the 38’-4” long existing joists (just under ½ of the joists length):
Lowering the addition is not allowed.
Framing a new roof on top of the existing roof is not allowed.
Any type of reinforcing inside of the prohibited space is not allowed due to access issues.
In talking this over with my colleague, we have come up with a method that may work… although it is a little sketchy. We are proposing to introduce new beams in-between the existing roof joists. These members will only be applied above the space that we can access (which is roughly the length of the snow drift). These new members will be supported by stub columns and new support beams that will be 4” below the existing joist bottom chord (this is to allow the existing joists to deflect and not be accidentally supported by the new support beam and cause a stress reversal in the existing joist).
I think this is the best solution that we can possibly come up with. It checks off lots of boxes, however, I am slightly nervous about introducing a new support system in-between the existing joists that will be supported at mid span of the existing joists (thinking that we may still end up with some stress reversal due to increase stiffness of the support system at this location). I can easily design the new support system to support all of the loads in the bay if necessary.
Does anyone have any comments on the proposed plan? Has anyone attempted a similar method of reinforcement in the past?