I am in the process of designing a splitter wall (7' concrete spread footing wall)and a filtration chamber (11'L interior X 4'W interior X 12'H open top concrete box which is subject to soil on one side and water on 3 sides)for a detention pond.
Q1. According to the publication "Strength Design for Reinforced-Concrete Hydraulic Structures"by USACE, load factor for fluid pressure should be increased to 1.7 from 1.4 (ACI318). Inaddition, 1.3 will need to be applied to the factored load. This publication was adapted from ACI 350R-89. Since I don't have a copy of ACI 350R-89, I wonder if I could use load factor of 1.4 instead of 1.7, though I believe 1.3 needs to be applied according to ACI 350R-89.
Q2. Is there any special requirement on reinforcement and concrete. The USACE says ASTM Grade 60 is to be used. What are the concrete specifications?
Thanks.
Q1. According to the publication "Strength Design for Reinforced-Concrete Hydraulic Structures"by USACE, load factor for fluid pressure should be increased to 1.7 from 1.4 (ACI318). Inaddition, 1.3 will need to be applied to the factored load. This publication was adapted from ACI 350R-89. Since I don't have a copy of ACI 350R-89, I wonder if I could use load factor of 1.4 instead of 1.7, though I believe 1.3 needs to be applied according to ACI 350R-89.