DJCherre
Chemical
- Aug 11, 2004
- 7
Folks,
We have several shell & tube kettle-type heat exchangers where propylene refrigerant is in the shell, process in the tubes. The propylene is flashed to either 70 psig (35 degF) or 6 psig (-40 degF), depending on the exchanger. The level indication/control of the refrigerant is lousy, so they all run in manual. What we currently have is dP level indication. In one instance both impulse lines are insulated & steam traced and in another they're not insulated & are hapazardly steam traced. We recently replaced dP with guided wave Radar & insulated the stilling well. It's better, but still not under control and still spikes up & down a lot. So, I wonder if anyone has any suggestions for refrigerant level control in south Louisiana.
Thanks,
Dean
We have several shell & tube kettle-type heat exchangers where propylene refrigerant is in the shell, process in the tubes. The propylene is flashed to either 70 psig (35 degF) or 6 psig (-40 degF), depending on the exchanger. The level indication/control of the refrigerant is lousy, so they all run in manual. What we currently have is dP level indication. In one instance both impulse lines are insulated & steam traced and in another they're not insulated & are hapazardly steam traced. We recently replaced dP with guided wave Radar & insulated the stilling well. It's better, but still not under control and still spikes up & down a lot. So, I wonder if anyone has any suggestions for refrigerant level control in south Louisiana.
Thanks,
Dean