Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Refrigerant level control

Status
Not open for further replies.

DJCherre

Chemical
Aug 11, 2004
7
Folks,
We have several shell & tube kettle-type heat exchangers where propylene refrigerant is in the shell, process in the tubes. The propylene is flashed to either 70 psig (35 degF) or 6 psig (-40 degF), depending on the exchanger. The level indication/control of the refrigerant is lousy, so they all run in manual. What we currently have is dP level indication. In one instance both impulse lines are insulated & steam traced and in another they're not insulated & are hapazardly steam traced. We recently replaced dP with guided wave Radar & insulated the stilling well. It's better, but still not under control and still spikes up & down a lot. So, I wonder if anyone has any suggestions for refrigerant level control in south Louisiana.
Thanks,
Dean
 
Replies continue below

Recommended for you

Dean
We are using similar liquid (Pentane) in close loop system where it boiled in one heatexchanger and condensed in another one. We need to keep the level at the boiler which is tube and shell heatexchanger by controlling the pump supplying the liquid. The best solution I found is the DP transmitter. Due to the nature of the liquid and the low pressure measured, it must be equipped with two diaphragm seals each with 2” or (Preferable 3”) 150 or 300# flanges. Best performances we got from Rosemount, Smar, Yokagawa, DP with integral Diaphragm seals.
ilan
 
Dean
We are using similar liquid (Pentane) in close loop system where it boiled in one heatexchanger and condensed in another one. We need to keep the level at the boiler which is tube and shell heatexchanger by controlling the pump supplying the liquid. The best solution I found is the DP transmitter. Due to the nature of the liquid and the low pressure measured, it must be equipped with two diaphragm seals each with 2” or (Preferable 3”) 150 or 300# flanges. Best performances we got from Rosemount, Smar, Yokagawa, DP with integral Diaphragm seals.
We have one unit not far from Morgan City LA.
Regards
ilan
 
By diaphragm seals are you referring to what we call "pressure pads" or "remote seals"? Where the pressure-sensing diaphragm is on the end of a tube-like gizmo that you slide into the flange, right up to the process. That sounds like a great idea, since the big problem we're having is the flashing/condensing of propylene refrigerant in the impulse lines. The seals would eliminate the impulse lines.
Thanks for the response!
Dean [pipe]
 
you should have filled impulse lines in this service, not filled with liq. refigerant, but with non-freezing liquid

the remote seals work too as long as you mak provision for valved isolation from the process for maintenance.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor