For rebar (say #4 or #5 bar) being used as a shear dowel for concrete floor deck, are the equations for shear capacity the same as anchor bolts? This is being used to transfer diaphragm forces to cmu shear wall. I attached a pic I found online. Thanks
 
Replies continue below

Recommended for you

This short horizontal bar is far less needed for shear rather than just to keep the PT plank from separating from the CMU wall - the same condition as anchoring a wood joist to a concrete wall.

I believe the concrete section itself would provide adequate shear in most cases with out the steel having to be being considered.