Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Rebar attachment to sheet pile wall 1

Status
Not open for further replies.

gf12

Structural
Mar 24, 2005
1
Hi,

I was wondering if anyone is familiar with attaching Reinforing bars to Z shaped sheet piling.

I have a sheet pile retaining wall that is getting a cast in place concrete facing for the portion above grade. I would like for the horizontal rebar nearest to the steel sheeting to be attached.

Any info would be greatly appreciated

Thanks
 
Replies continue below

Recommended for you

Where we have put a concrete face on steel sheetpiling, we have welded Nelson Studs to provide a positive conection between the sheest and the concrete. The stud locations are ground to clean metal and welded with either a gun or by stick. The face is then reinforced with 1 or 2 mats of rebar. If you do weld rebar to the sheets specify weldable rebar ( I think it is A706) A615 can become brittle if welded.
 
DRC1 is correct. Use Nelson shear studs with the double rebar mat. Studs should be 3/4" maximum diameter and should extend beyond the closer rebar mat.
 