TurbineBlade
Nuclear
- Aug 23, 2006
- 44
Hi,
I am performing a temporary modification to create a tie-in to an existing cooling water system (150 psig, 100C) involving adding a small booster pump (operating point at 20 psi, 11 L/s) in a branch circuit (3" line). I plan to use the existing system design pressure and temperature for the modification. The normal system operating pressure is 100 psig.
1) If the existing system operates say (144 psig) due to an upset, which is just below the setpoint 145 psig of the existing RV. My modification with the booster pump operates at 144+20 = 164 psig, which exceeds the design pressure. I have no place to divert the water to a drain from the pump discharge. I put a PRV in the pump re-circulation, which set to open at 145 psig and divert the fluid back to the pump suction at 5 L/s + the operating path (11 L/s) = 16 L/s @ 5 psi. The pump will be at run off condition. This will keep the pressure within the design pressure.
Since the back pressure is higher than 50%, the vendor suggests using a pilot operating PRV (1.5"x3"). I would like to ask if there is other way to solve this problem as I read putting a RV in the pump re-circulation line which is not a common practice.
Turbineblade
I am performing a temporary modification to create a tie-in to an existing cooling water system (150 psig, 100C) involving adding a small booster pump (operating point at 20 psi, 11 L/s) in a branch circuit (3" line). I plan to use the existing system design pressure and temperature for the modification. The normal system operating pressure is 100 psig.
1) If the existing system operates say (144 psig) due to an upset, which is just below the setpoint 145 psig of the existing RV. My modification with the booster pump operates at 144+20 = 164 psig, which exceeds the design pressure. I have no place to divert the water to a drain from the pump discharge. I put a PRV in the pump re-circulation, which set to open at 145 psig and divert the fluid back to the pump suction at 5 L/s + the operating path (11 L/s) = 16 L/s @ 5 psi. The pump will be at run off condition. This will keep the pressure within the design pressure.
Since the back pressure is higher than 50%, the vendor suggests using a pilot operating PRV (1.5"x3"). I would like to ask if there is other way to solve this problem as I read putting a RV in the pump re-circulation line which is not a common practice.
Turbineblade