Dear Readers,

We are looking at using a burner to bring a reactor up to temperature of 650°C and then turning off the burner as the process becomes self sustaining. To reduce down time when a feed shut down occurs, we would like to restart the burner to avoid having to cool the whole system down to air temperature. I have been told that the burner would not be allowed (under regulations) to restart if the temperature in the reactor is under 700°C. Could someone please confirm this temperature and let me know which regulations would mention this limit?

Thank you very much!
 
Replies continue below

Recommended for you

The "regulation" you refer to, is NFPA 86, which states that when you can't auto-ignite(because your chamber, furnace, oven, etc. isn't hot enough ~850C), you have to have a flame safety system in place so you don't allow gas to build up. This is a common control sequence that will confirm the operation of the safety shut-off valves, a trial for ignition, and flame check. This whole sequence should take 2-5 minutes. Further, whoever you buy the burner from should be able to spec out the controls needed.
 
Hi Al,

Thanks for the information. I also looked-up BS EN 746-2 and the requirement there if for 750°C.

Cheers.
 