R factor for two different structural systems

Status
Not open for further replies.

lesgiu

Structural
Jul 20, 2001
14
Hello,

I'm doing the structural evaluation of a 3-story building that has in one direction only confined masonry. For earthquake loads the building doesn't comply with any requirement and we are adding concrete shear walls. During the evaluation I used an R factor of 3 but now that I have added new concrete shear walls I wonder if I can increase the R factor to 6? or should I keep it as R=3?

I would appreciate if you can give me your comments.

Thanks
 
Replies continue below

Recommended for you

If you ignore the existing CMU, 6. Otherwise 3.

Mike McCann
MMC Engineering

 
If you are designing the system to comply with the increased R factor then you should use the increased R factor. I have a current project where the client wants to use 2 walls of an existing URM building in his new structure (due to permitting concerns). I utilizing braces for the LFRS of the new building. I am not relying on the existing URM and have told the client that the existing URM now need to be attached to the new structure as if was a facade and that is how I am looking at the URM section of the new building. Kind of cheap... but as far as I can tell allowed by the code.
 