rgvrider
Mechanical
- Sep 6, 2009
- 26
Hi,
I have a somewhat interesting problem involving pumping water downhill. I have a system which has a static drop of about 6m from inlet to outlet, with a slight crest rise (2m) in the middle, hence the need to a pump system.
I've modeled a power trip simulation for water hammer. The pipe line is 3", with flow about 4 l/s. With very small inertia, the pump rapidly stops on a power trip. Not surprisingly, this results in close to full vacuum pressure and vapor formation.
My question is: Given I have vapor formation, and resultant rapid volume change on pressure rise and associated pressure spikes, should I be worried if the pipe is designed for vacuum and the modeled pressure spikes are well within pipe design?
Pipe is buried and well anchored.
Cheers.
I have a somewhat interesting problem involving pumping water downhill. I have a system which has a static drop of about 6m from inlet to outlet, with a slight crest rise (2m) in the middle, hence the need to a pump system.
I've modeled a power trip simulation for water hammer. The pipe line is 3", with flow about 4 l/s. With very small inertia, the pump rapidly stops on a power trip. Not surprisingly, this results in close to full vacuum pressure and vapor formation.
My question is: Given I have vapor formation, and resultant rapid volume change on pressure rise and associated pressure spikes, should I be worried if the pipe is designed for vacuum and the modeled pressure spikes are well within pipe design?
Pipe is buried and well anchored.
Cheers.