I am designing a gas chiller with sour natural gas in the tubeside (DP: 455 Psig) and boiling propane on the shellside (DP: 225 Psig).
Q1: Since the 455 is more than 1.3X the 225, at first glance it would seem that I need a tube rupture PSV. However, API-521 has a statement about using tubeside operating pressure instead of design - my op is only 166 Psig. Do I still need provision for a tube rupture PSV? Since the chiller is outside and propane filled, I will probably have to do a firesize on this as well.
Q2: Due to compressor controls, the tubeside can be isolated with auto-closing block valves. Do I need to consider a tubeside fire case even though the bundle is submerged in liquid boiling propane? If it is blocked in and begins to warm up, the pressure will rise.
Help?
Q1: Since the 455 is more than 1.3X the 225, at first glance it would seem that I need a tube rupture PSV. However, API-521 has a statement about using tubeside operating pressure instead of design - my op is only 166 Psig. Do I still need provision for a tube rupture PSV? Since the chiller is outside and propane filled, I will probably have to do a firesize on this as well.