Situation:
We have a remote steam line 300# and the only place remove the condensate from the live line is into a nearby oil line which has a lower rating of 150#.
The oil system has other ASME vessels in it that need to be safeguarded from the higher pressure steam line in the event that:
1. 1-inch stream traps breaks
2. accidental opening of 1-inch by-pass valves
Other issues:
1. Simulation results show that when steam flows into the oil pipeline, it would flash some of the lighter ends in the oil pipeline and result in an over all vapour fraction of 20%
2. This flashed fluid has a very high 2-phase volumetric flow, which would push the oil out the other end, but because the other end of the line has not heated up in the instant of the upset event, this volumetric 2-phase flow will push an equivalent flow of single phase liquid oil.
3. When we size the PSV for the single phase mass flow rate of oil to be relieved using a PSV, the PSV orifice size is very large than one would expect from failure of 1-inch trap or valve
Concern:
1. Is there a normal set of assumptions used when sizing PSV for upstream steam trap failures?
2. How does one calculate the flow of steam though a steam trap whose vendor data is only for flow of liquid condensate?
We have a remote steam line 300# and the only place remove the condensate from the live line is into a nearby oil line which has a lower rating of 150#.
The oil system has other ASME vessels in it that need to be safeguarded from the higher pressure steam line in the event that:
1. 1-inch stream traps breaks
2. accidental opening of 1-inch by-pass valves
Other issues:
1. Simulation results show that when steam flows into the oil pipeline, it would flash some of the lighter ends in the oil pipeline and result in an over all vapour fraction of 20%
2. This flashed fluid has a very high 2-phase volumetric flow, which would push the oil out the other end, but because the other end of the line has not heated up in the instant of the upset event, this volumetric 2-phase flow will push an equivalent flow of single phase liquid oil.
3. When we size the PSV for the single phase mass flow rate of oil to be relieved using a PSV, the PSV orifice size is very large than one would expect from failure of 1-inch trap or valve
Concern:
1. Is there a normal set of assumptions used when sizing PSV for upstream steam trap failures?
2. How does one calculate the flow of steam though a steam trap whose vendor data is only for flow of liquid condensate?