the concern is regarding sizing a PSV for fire case for Glycol Cooler in Glycol Regeneration Package.
Data is as below:
1-PSV set pressure=10 barg
2-glycol cooler inlet conditions:temp=73 c,pressure=6.3 bar
3-glycol cooler outlet conditions:temp=37 c,pressure 5.8 bar
4-wetted surface area considering 20% margin for associated piping=70 ft^2
5-actual glycol flowrate=13.5 m^3/h
As far as I know the condition before relif in fire case is p=relief pressure(21% higher than set pressure) and temp=liquid boiling pressure.please correct me if I am wrong.
For glycol with purity about 99.2% mol the boiling point in 13.1 bara(21% above set pressure) is around 440c which is higher than design temperature for carbon steel(material of glycol cooler).
please explain me in depth the procedure for sizing PSV for such case.
Data is as below:
1-PSV set pressure=10 barg
2-glycol cooler inlet conditions:temp=73 c,pressure=6.3 bar
3-glycol cooler outlet conditions:temp=37 c,pressure 5.8 bar
4-wetted surface area considering 20% margin for associated piping=70 ft^2
5-actual glycol flowrate=13.5 m^3/h
As far as I know the condition before relif in fire case is p=relief pressure(21% higher than set pressure) and temp=liquid boiling pressure.please correct me if I am wrong.
For glycol with purity about 99.2% mol the boiling point in 13.1 bara(21% above set pressure) is around 440c which is higher than design temperature for carbon steel(material of glycol cooler).
please explain me in depth the procedure for sizing PSV for such case.