Msr.=Misure -Fr.
First let me add to the reasons above,
7.) Possible alteration or modification of plant equipment in future.
OK, had a look at B31.3 - but the 2002 edition. I give a summary of what I found,
*********************************************************
302.2.4 Self-limiting events +20% if < 50 hrs & 500 hr/yr
322.6.3 Liquid thermal expansion set pressure < test press and < 120% design pressure
322.6.3 Relieving apacity of any pressure relieving device shall include consideration of all piping systems which it protcts.
322.6.3 (2) Liquid thermal expansion relief device which protects only a blocked-in portion of a piping system, the set pressure shall not exceed 120%
******
Chapter VII Nonmetallic Piping and Piping LIned with Nonmetals
A302.2.4 (a) nonmetallic - variations above P & T not permitted.
A302.2.4 (b) metallic lined - permitted if lining sutiable
******
Chapter VIII Category M Fluid Service
M302.2.4 Allowances in para. 302.2.4 is not permitted.
M322.6.3 Metallic piping - 110% of design pressure during operation of a pressure relieving system.
*****
Chapter IX High Pressure Piping
K302.2.4 variations in pressure above the design pressure not permitted, except during relieving
K322.6.3 (a) capacity of ? relieving devices must prevent pressure rise above 10% of design pressure AT operating Temp for 1 relieving device. No more than 16% above with >1 relief device. IF 1 device is set to D.P. and none set higher than 105% of design pressure.
(c) Supplementary pressure relieving devices provided
for protection against overpressure due to fire
or other unexpected sources of external heat shall be
set to operate at a pressure not greater than 110% of
the design pressure of the piping system and shall be
capable of limiting the maximum pressure during relief
to no more than 121% of the design pressure.
*********************************************************
B31.4 Transportation Systems for Liquid Hydrocarbons and other Liquids
402.2.4 Ratings - Allowance for Variations From
Normal Operations. Surge pressures in a liquid pipeline
are produced by a change in the velocity of the moving
stream that results from shutting down of a pump
station or pumping unit, closing of a valve, or blockage
of the moving stream.
Surge pressure attenuates (decreases in intensity) as
it moves away from its point of origin.
Surge calculations shall be made, and adequate controls
and protective equipment shall be provided, so
that the level of pressure rise due to surges and other
variations from normal operations shall not exceed the
internal design pressure at any point in the piping
system and equipment by more than 10%.
************************************************
B31.8
805.217 Overpressure protection is provided by a device or equipment installed for preventing the pressure in a pressure vessel, a pipeline, or a distribution system from exceeding a predetermined value. This protection may be obtained by installing a pressure relief station or a pressure limiting station.
843.411 Pressure relief or other suitable protective devices of sufficient capacity and sensitivity shall be installed and maintained to ensure that the masximum allowable operating pressure of the station piping and equipment is not exceeded by more than 10%.
843.442 Relief is required immediately after +displacement compressor or on pipeline.
=============== my conclusion is ===========================
Given the above posts, The B31.3 code appears to agree with BVP VIII in this respect.
B31.3 does not agree with B31.4 nor B31.8
Both B31.4 and 8 limit maximum pressures to 10% higher than design pressure.
B31.3 permits variations well in excess of 10% overpressure under some circumstances. Of note are the many possible allowances well above 10%, "with permission of the owner". The pipeline codes have no provision to exceed 10% overage under any circumstance. And in the USA, CFR 49, Parts 192 & 195 would legally prohibit a regulated pipeline from that practice.
************************************************
IMO all the abov tend to justify separate relief installations in between any facilities that are not immediately associated with a pipeline or pipeline pump or compressor station. That IMO could not possibly include any facility designed to B31.3, given the many exceptions to the 10% pipeline overpressure limit sumarized above.
I have always ordered PSVs on vessels associated with pipeline work to be fitted with PSVs set to a max of 10% over the design pressure and have always protected pipelines and associated facilities independently of liquid plant and refinery systems. I don't believe it is safe to do otherwise, esp. in the long term where changes and modifications can often occur without any exchange of information between pipeline company and refinery or liquid plant, power plant operators, etc.
I would like to hear other's opinions about this.
BigInch
![[worm] [worm] [worm]](/data/assets/smilies/worm.gif)
-born in the trenches.