can I ask what this connection is on?
It looks like a crane runway girder.
Anyway, I agree with hokie.
This connection should have a pair of stiffeners. It looks to be an "unframed end" of beam in which case I believe AISC requires stiffeners for rotation anyway.
Rotational Restraint at Support
AISC Specification Section J10.7 requires full-depth stiffeners at the “unframed ends of beams and girders.” What does this mean? Would an example be a girder bearing on a column with no beam framing into it at the column?
Answer
Yes, this section addresses situations such as the end of a beam that bears on column cap plate. Unless the column top is restrained, the beam might twist or the web might distort, allowing the bottom flange to move transversely. This creates a dangerous situation, because the column below was designed assuming a pinned-pinned condition with its top is restrained against lateral displacement. If a brace is provided to restrain the top of the column, the beam end is framed. If not, stiffeners can be used as required in Section J10.7. Note that the concern for column stability also exists when girders frame continuously over the top of the column. See Section 2 of the 13th edition AISC Steel Construction Manual for further information.
Brad Davis, Ph.D., S.E.