8.15.3 Stairways.
8.15.3.1 Combustible Construction. Sprinklers shall be installed beneath all stairways of combustible construction.
8.15.3.1.1 Sprinklers shall be installed at the top of combustible stair shafts.
8.15.3.1.2* Sprinklers shall be installed under the landings at each floor level.
A.8.15.3.1.2 Sprinklers at each floor level landing should be positioned to protect both the floor level landing and any intermediate landing.
8.15.3.1.3 Sprinklers shall be installed beneath the lowest intermediate landing.
The requirement for sprinklers to be installed under “all stairways” needs to be clarified. In stairs with both floor landings and intermediate floor landings, the interpretation has been that the sprinklers need to be installed under both, but that would be overkill. The committee believes the original intent of this section was to provide protection at the floor landings.
Finally, clarification was needed in protecting exterior combustible stairs, so additional language was added for requirements on the location of sprinklers at the floor landings. Combustible stair shafts must be entirely protected irrespective of storage capability or exterior location.
8.15.3.2 Noncombustible Construction.
8.15.3.2.1 In noncombustible stair shafts having noncombustible stairs with noncombustible or limited-combustible finishes, sprinklers shall be installed at the top of the shaft and under the first accessible landing above the bottom of the shaft.
FAQ Why are sprinklers required in noncombustible stair shafts at the top of the shaft and under the first landing above the bottom of the shaft?
The storage of materials in stairwells obstructs the egress route and is prohibited by NFPA 101. However, if there is an open space under the first landing or a large landing at the top of the stairs it is often an irresistible location for transient storage. As a result, 8.15.3.2.1 requires sprinklers at these locations.
8.15.3.2.2 Where noncombustible stair shafts are divided by walls or doors, sprinklers shall be provided on each side of the separation.
8.15.3.2.3 Sprinklers shall be installed beneath landings or stairways where the area beneath is used for storage.
8.15.3.2.3.1 Sprinklers shall be permitted to be omitted from the bottom of the stairwell when the space under the stairs at the bottom is blocked off so that storage cannot occur.
The concept of eliminating the sprinkler at the bottom of the stairs has always been implied by NFPA 13, but the statement was never made explicitly in the text. Where the egress path is the only available space in the stairwell, sprinklers should not be necessary. This makes it very clear that when the area beneath the bottom landing is blocked off, sprinklers are not required in the bottom of the stairwell. In the past, many authorities having jurisdiction still required sprinklers to be provided under the 2nd floor main landing even when the space at the bottom was blocked off.
8.15.3.2.4 Sprinklers shall be permitted to be omitted from exterior stair towers when the exterior walls of the stair tower are at least 50 percent open and when the stair tower is entirely of noncombustible construction.