Our testing found the the freezing point of the prop/water mixture was -15F. From the chart found on the net below the mixture is approximately 46% prop/ 54% water
Freezing Point
Propylene Glycol Solution
(% by mass) 30 40 50 60
Temperature 7 -8 -29 -55
The operating temperature of the mixture is 45 deg F. The application is an air cooled chiller. The system as installed did not have a flow measuring device installed in the piping. During a recent shutdown a nexus twin-tube pitot
was installed in a nice straight run of 3" pipe.
Our testing indicated that the pressure drop across the twin tube was 8" wc. In the flow chart provided in the link below the flow for a 3" twin tube w/ an 8" delta P is 100 GPM based on water at 60 deg F.
Question:
1)What is the correction factor for the flow rate of mixture based on the data given above?
2) If there is a "layman's version" of the criteria that are used to develop the correction factor, I'd be interesting in hearing it.
Thanks
Mark
Freezing Point
Propylene Glycol Solution
(% by mass) 30 40 50 60
Temperature 7 -8 -29 -55
The operating temperature of the mixture is 45 deg F. The application is an air cooled chiller. The system as installed did not have a flow measuring device installed in the piping. During a recent shutdown a nexus twin-tube pitot
was installed in a nice straight run of 3" pipe.
Our testing indicated that the pressure drop across the twin tube was 8" wc. In the flow chart provided in the link below the flow for a 3" twin tube w/ an 8" delta P is 100 GPM based on water at 60 deg F.
Question:
1)What is the correction factor for the flow rate of mixture based on the data given above?
2) If there is a "layman's version" of the criteria that are used to develop the correction factor, I'd be interesting in hearing it.
Thanks
Mark