hello people....
I am an assistant engineer in TESTING AND COMISSIONING. I have tested REF relay and the full scheme in HIGH IMPEDANCE method. I heard that there are some other methods too for REF scheme testing. The method which i use to check is like
FOR STABILITY
i used a primary current injection set and made current to flow through two CT's(one phase and another neutral CT) and no spill current is observed.
FOR SENSITIVITY
made primary current to flow through only one CT(each phase CT's and neutral CT's) and the spill current is observed in relay and followed by trip.
some other method i heared is like shorting one winding(ex star secondary in DYn TRX) and injecting voltage on the other winding(ex delta primary). Am not sure of this method and will be helpfull if any one give an answer for this in some detailed manner.I just need the testing procedure alone. (for distribution DYn TRANSFORMER,1500kva,11/0.415 KV) Thanks in advance.
I am an assistant engineer in TESTING AND COMISSIONING. I have tested REF relay and the full scheme in HIGH IMPEDANCE method. I heard that there are some other methods too for REF scheme testing. The method which i use to check is like
FOR STABILITY
i used a primary current injection set and made current to flow through two CT's(one phase and another neutral CT) and no spill current is observed.
FOR SENSITIVITY
made primary current to flow through only one CT(each phase CT's and neutral CT's) and the spill current is observed in relay and followed by trip.
some other method i heared is like shorting one winding(ex star secondary in DYn TRX) and injecting voltage on the other winding(ex delta primary). Am not sure of this method and will be helpfull if any one give an answer for this in some detailed manner.I just need the testing procedure alone. (for distribution DYn TRANSFORMER,1500kva,11/0.415 KV) Thanks in advance.