Yes, sorry. I couldn't view the drawing from where I was earlier. That definitely is a 2-phase soft starter, very bad for a motor that has any kind of load on it. I've seen them used successfully on centrifugal pumps and fans, but still, I agree with LionelHutz, I would not use them in my motors, especially 50kW.
Another inherent danger on that design is a shorted SCR. If you have a 6-SCR design soft starter and one SCR shorts, it's not immediately dangerous to the motor because there is no complete circuit path. But in this design, 1/2 of the circuit path is ALWAYS present, so a single shorted SCR immediately results in unrestricted current flow into one winding.
In addition, SCRs can "self commutate" (turn themselves on) if there is a high dv/dt situation, such as high noise spikes on the line. Normally because you would need to have at least TWO of the SCRs self commutate for that to be a complete circuit, it's not much of a problem. But again, because 1/2 of the complete circuit is ALWAYS present here, it can be.
At the very least, I would put isolation contactors ahead of these soft starters so they are truly off-line when not being used. Ideally, junk them and start over with a 6 SCR designed soft starter.