Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Pressurization Problem

Status
Not open for further replies.

LDRoofing

Structural
Joined
Jul 28, 2003
Messages
1
Location
US
Having a problem with HVAC Unit. Unit pressurized building and caused air to filter through acoustical roof deck and balloon rubber roof rendering roof defective. Has anyone ever seen this before? If so, has there been any documentation on it? Where could I find such articles/cases? Please help!

is my company.
 
I have seen this occur, although the roofing membrane remained in-tact. It just ballooned. The problem was fixed by closing ventilation damper. Fortuneately the lack of occupants in the space allowed for this. Otherwise a way to relieve the pressure will be required. This can be achieved by adding barometric damper to the outdoor unit or an powered exhaust fan.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top