Aug 22, 2013 #1 Lc85 Electrical Joined Apr 14, 2011 Messages 107 Location GB We have an abb 266hsh and the sensor span limits are 0.65 and 65kPa. am i correct in assuming that our calibrated range of -10 to 10 kPa will be fine for this transmitter as it falls within these limits? thanks
We have an abb 266hsh and the sensor span limits are 0.65 and 65kPa. am i correct in assuming that our calibrated range of -10 to 10 kPa will be fine for this transmitter as it falls within these limits? thanks
Aug 22, 2013 #2 danw2 Industrial Joined Oct 21, 2004 Messages 1,528 Location US Yes. The spec sheet gives the range as -65kPa to +65kPa with a minimum span of 0.65kPa. Your range of -10 to +10kPa exceeds the minimum span and falls within the stated range. Upvote 0 Downvote
Yes. The spec sheet gives the range as -65kPa to +65kPa with a minimum span of 0.65kPa. Your range of -10 to +10kPa exceeds the minimum span and falls within the stated range.