Precast Double Tee Bearing Displacement
TRAK.Structural
335
A contractor client sent me some photos of a precast parking deck that has some damage. At one location it looks like the bearing connection at the end of a double tee has failed and the tee has displaced. Can't tell from the picture if this double tee has a dapped end or not. Has anyone seen something like this before? Are there any resources out there from PCI that show common bearing end details and common repair schemes for these types of structures?
At this point, you probably need to retrofit a corbel anchored into the wall or a pilaster to the floor to support it.
To avoid future problems, you'll need to determine what moved, and mitigate it.
A new corbel would put moment into the supporting wall that likely would not have been accounted for in the design of the wall. A new pier, anchored to the wall and extending down to the foundation would have to pass through the "floor" of lower levels which seems like would be a huge pain.
Looks less like something moved and more like the bearing spalled off allowing it to fall straight down.
Water running down through from above (where it's obviously wet) and rusting those bars and blowing out the concrete seems likely. The fix will likely be a pain. But a lot less painful than that thing falling on your head.
Yea that's my first impression too. Looks like there may be some cracking around where the flange/slab meets the web which would be my biggest concern for being able to re-form the bearing and set the tee back in place.
You’d be surprised to know how often this happens to corbels, either because the design was bad or the rebar cage was misplaced in the form. Can’t say I’ve ever seen the flange delaminate like that (las photo). Scary. My vote is no dapped end. Jack it up and rebuild the wall/bearing, as a “bandaid.”
Looks like the contractor should get a shore under the web in photo #2 and #3 (photo #1 is a smaller version of photo 2).
Not sure what the black stuff is...could be some kind of fill...could be just a void.
Needs inspection to determine how much bearing is available and whether or not the web is dapped (doesn't look like it).
The simplest repair for #2 is to fill the gap with grout, if that is possible, and provided there is sufficient bearing on the wall. It looks like the wall was saw-cut to create space for the web.
Hard to say about #3, but it looks like the double tee is just hanging from the flange in that location. Need to find out.
It is possible a permanent shore is required in both locations. Needs a proper study.