salem

Electrical
Joined
May 2, 2001
Messages
38
Location
AE
Can we use a power transformer 50 Hz on a 60 Hz network
Transformer primary voltage ( 26-30-34)kV, secondary voltage 0.4 kV.
Network voltage 36 kV, 60 Hz
 
The flux will be the same at 36 kV/60 Hz as it is at 30 kV/50 Hz. But you will get about 480 V secondary if you connect that way. If that's what you want, then you are fine.

If you want about 400 V, you have to connect to the 34 V primary. You would then get about 424 V secondary if the internal voltage drop remained constant. Since your Uk will be about 20 percent higher, I guess that your full load voltage will be 415 - 420 V. Be warned that your idling voltage will be on the high side.

Your losses will increase slightly due to more magnetization losses and more eddy current losses. They increase with frequency.

 
You would have to reduce the operating voltage so that you do not exceed the transformer's design V/Hz rating. If the frequency is reduced by 5/6 then the maximum operating voltage must also be reduced by 5/6.
 