JPetersen
Electrical
- May 20, 2004
- 31
Dear friends,
We have a transformer, 3000kVA - step-down 6kV/0.4kV - cast resin - insulation class F.
Right now it is running at winding temp 130 deg. cel. (full load - PT100 embedded measurement). Ambient temperature is 20 deg. cel.
Ambient temperature is expected to reach approx. 35.
We expect to see winding temperatures of 130 + (35-20) = 145 deg. cel. when at 35 deg. amb.
Insulation class F allows a max. winding temp. of 155 deg. cel., and calculating with a hot spot temp. of +15 deg. cel. we unfortunately seem to be +5 deg. cel. on the wrong side.
What are your experiences with transformer winding temperatures? - will a 145 deg. cel. winding temp. be critical, or have any impact on lifetime?
At what temperature will the winding insulation break down instantly
Can you recommend any litterature on transformer winding temperatures and lifetime calculations?
Best Regards
J. Petersen
We have a transformer, 3000kVA - step-down 6kV/0.4kV - cast resin - insulation class F.
Right now it is running at winding temp 130 deg. cel. (full load - PT100 embedded measurement). Ambient temperature is 20 deg. cel.
Ambient temperature is expected to reach approx. 35.
We expect to see winding temperatures of 130 + (35-20) = 145 deg. cel. when at 35 deg. amb.
Insulation class F allows a max. winding temp. of 155 deg. cel., and calculating with a hot spot temp. of +15 deg. cel. we unfortunately seem to be +5 deg. cel. on the wrong side.
What are your experiences with transformer winding temperatures? - will a 145 deg. cel. winding temp. be critical, or have any impact on lifetime?
At what temperature will the winding insulation break down instantly
Can you recommend any litterature on transformer winding temperatures and lifetime calculations?
Best Regards
J. Petersen