Im working on an efficiency project and seek to gain some information to assist me with this. Hope that you can throw me some pointers for this.

Air flow temperature drop - If the air coming into an AHU is more than that leaving an AHU then there has been some temperature absorbed - how could this be worked into a watt figure - is this possible ? I know I need to get a l/s figure for the AHU and an adjustment figure for the pressure drop created by the filter media. But would this be a viable way to take this forward ?

Rugged
 
Replies continue below

Recommended for you

Just ignore all and use Q = 1.08 x cfm x dT, dT in deg.F. This give the heat in btus.

 