RJN3959
Structural
- Mar 3, 2014
- 1
I am looking for information on determining the concrete pullout strength for a post installed anchor. My situation is a little out of ordinary. I am very familiar with ACI 318 Appendix D however my situation is not covered. I have a steel bracket bolted to concrete. The bracket load induces a moment on the connection. The moment is transfered via tension in a post installed mechanical wedge anchor and compression between the edge of bracket and the concrete. The tension load on the anchor is about 4 times the external load due to the prying. The tensile load on the anchor and the compressive load on the concrete are typically 1 to 2" apart. The anchors are embedded 3 to 4" so the compressive load falls into the concrete breakout cone(mode that always controls the design). I know this compressive load will help with the concrete breakout but I do not believe it is as simple as taking the differnce between the anchor tensile laoding and the compressive concrete loading as the loads are not concentric. Anyone aware of any methods or references for this scenario?
thanks